PSS T & D SUBSTATION – QUALITY MANAGEMENTABB LTD.

1) INTRODUCTION

This guideline is prepared in view of the requirements for switchyard service inspection (visual) and condition based maintenance of substation equipments, structures and other miscellaneous items in substations. These guidelines are necessarily general. It is recommended to carry out maintenance of equipment as per manual supplied by manufacturer. All inspections and test procedures should also be performed in accordance with applicable codes and standards.

The aim of this guideline is to provide in general visual inspection check points for the structures, grounding systems, LT switchboards, etc. for which as such there is no readymade guidelines available. Also to provide the visual inspection and condition based maintenance of Major equipments like Transformer, Circuit breakers, CTs, CVTs, PTs, Disconnectors and LAs etc. to verify the health of the equipments.

Service visual inspection is the necessary activity to identify any visible abnormality or failure and require to be performed at specified interval. Whereas condition based monitoring checks (on line/ off line) are necessary to identify internal defects or abnormality, so that necessary preventive action can be taken up.

2) SERVICE INSPECTION & CONDITION MONITORING GUIDELINE

The substation in total and the inpidual items of equipment contained therein should be periodically inspected. Binoculars should be used to view buses and other equipment located on structures.

Painting and Galvanizing (Applicable to all equipments and systems)Depending on geographical location, local environmental condition, periodic inspection of painting and galvanizing condition of structures, panels, equipments etc. is required. Inspect for paint condition, damage paint, chalking effect, rusting etc. If any damage observed, do necessary repaint or repair work.

Grounding System

Check for loose connections of all ground connections at equipments, structures, panels, other equipments etc. Check for any sparking marks at termination or joint. Observe the condition of any flexible braid type connections for damage. Tighten the connections, clean the joints and replaced if found damage. Earth pits should be kept wet so as to have low resistance. Measure overall ground grid resistance. The Value obtained should be comparable with initially measured values or designed values.Structure

Inspect all the structures for loose or missing bolts or nuts. Observe any damage paint/ galvanizing or signs of corrosion. Inspect for deterioration, bending, buckling and cracking.

Civil work-Foundation and Control Room

Inspect for sings of settlement, cracks, spalling, honeycombing, exposed reinforcing steel, and anchor bolt corrosion. Check for break/ missed cable trench cover. Inspect for any crack/ leakages in control room and water tank. Check for proper functioning of sump pump and drainage system.

Buses and Shield wire

Inspect for loose clamps or connections. Inspect for bending of Alu-tube bending. Observe the condition of flexible buses and shield wires for any damages.

Porcelain Insulators and Bushings (For Bus post / Suspension / Circuit breaker / CT / CVT / PT & Transformer bushings)

Inspect all insulators and equipment bushings for chipped petticoats and fractured or cracked porcelain. Flashover in the past may have damaged a portion of the glazing on the porcelain. Make this inspection at close range. Replaced damage bushings. Remove dust and dirt from porcelain insulators with suitable methods. Cable

Inspect exposed sections of cable for physical damage. Inspect the insulation or jacket for signs of deterioration. Check for loose connections, lugs, tightness, cracking of lugs etc. Inspect shield grounding (where applicable), cable support and termination. Check for any sparking marks at termination or joint. Clean sparking marks if any and make proper joint with proper tightening and lugging.

LT Cable & Metal clad switchgear (Control-Metering, Relay panel, Outdoor and indoor panel)

Examine meters, relays and instruments externally to check for loose connections and damage to cases and covers. Check whether the instruments are reading or registering. Check the functioning of annunciator panels. Inspect for damage to enclosures, doors, latching mechanisms, locks etc. Check out for burned-out lamps.

Battery and battery chargerCheck for any physical damage, loose connections. Check for low level or low specific gravity of the electrolyte. Record the electrolyte temperature. Verify vent cap and flame arresters are in place. Check electrolyte appearance. Check working of exhaust fan.Check for cleaning and corrosion.Observe temperature (by touch). If temperature is found high, check and attend the reason for the same. Check the charging current and voltage. Observe the ground detector lamps for an indication of an undesirable ground on the dc system. Compressor

Check for leakage of air. Check air pressure and Oil level. Substation area- General

Verify the existence of appropriate danger and informational warning signs. Verify whether they are missing or needs repainting.

Check for rusting of fasteners

Check for any hotspots at conductor/ equipment/ stringing termination.

Check for indoor and outdoor lighting systems for burned-out lamps or other component failures

Verify that there is adequate supply of sparesInspect the fire protection system

Check for bird/ animal nests or other foreign materials in the vicinity of energized equipment, buses or fans.

Observe the general condition of the substation yard, overall cleanliness

Observe the position of all circuit breakers in the auxiliary power system and verify the correctness of this position (indication on breaker).

Inspect t …… 此处隐藏:7896字,全部文档内容请下载后查看。喜欢就下载吧 ……

ABB-Substation-Condition-Monitoring-Schedule.doc 将本文的Word文档下载到电脑,方便复制、编辑、收藏和打印
本文链接:https://www.jiaowen.net/wendang/1412944.html(转载请注明文章来源)
Copyright © 2020-2025 教文网 版权所有
声明 :本网站尊重并保护知识产权,根据《信息网络传播权保护条例》,如果我们转载的作品侵犯了您的权利,请在一个月内通知我们,我们会及时删除。
客服QQ:78024566 邮箱:78024566@qq.com
苏ICP备19068818号-2
Top
× 游客快捷下载通道(下载后可以自由复制和排版)
VIP包月下载
特价:29 元/月 原价:99元
低至 0.3 元/份 每月下载150
全站内容免费自由复制
VIP包月下载
特价:29 元/月 原价:99元
低至 0.3 元/份 每月下载150
全站内容免费自由复制
注:下载文档有可能出现无法下载或内容有问题,请联系客服协助您处理。
× 常见问题(客服时间:周一到周五 9:30-18:00)